    Post Hi, uploading from AB 1400, notification pops, program in the process has changed

    Hi please, am trying to upload a program from PLC AB 1400.after uploading, a message pops up asking me if I wish to go online,
    when i accept another message pops up saying program in the processor has changed causing an offline state, do i want to upload ?

    please will appreciate any help

  2. #2
    Administrator Shawn Tierney's Avatar
    Join Date
    Sep 2016
    Location
    Berkshires, MA
    Posts
    2,228
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks Thanks Given 
    11
    Thanks Thanks Received 
    2
    Thanked in
    2 Posts
    Good morning @EPHRAIM,

    As you can see in my article and video (link below) this typically does not happen:

    https://theautomationblog.com/how-to...crologix-1400/

    So if you need help finding what is causing the issue, we'll need more information, like:

    If you select yes, does the same thing happen?

    If you say no, can you view the program offline?

    Are you directly connected via Ethernet, or going through a switch which also connects to other devices?

    What mode is the PLC in?

    What versions of Windows, RSLinx, RSLogix are you using?

    Shawn Tierney,
    Instructor at The Automation School
    Looking for affordable automation training? If you are, check out my courses at TheAutomationSchool.com!

  3. #3
    Member EPHRAIM's Avatar
    Join Date
    Jan 2019
    Posts
    4
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Thanks Thanks Given 
    0
    Thanks Thanks Received 
    0
    Thanked in
    0 Posts
    thank you for the reply sir,
    If you select yes, does the same thing happen? once i press yes it goes gain asking me to create a new file, then save, after do you want to go online if yes the same information appears
    If you say no, can you view the program offline? i cant without saving
    Are you directly connected via Ethernet, or going through a switch which also connects to other devices? directly connected to Ethernet
    What mode is the PLC in? RUN mode
    What versions of Windows, RSLinx, RSLogix are you using? window 7 professional 32 bit, RSLinx 2.75, RSLogix 8.10.00 CPR 9

  4. #4
    Administrator Shawn Tierney's Avatar
    Join Date
    Sep 2016
    Location
    Berkshires, MA
    Posts
    2,228
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks Thanks Given 
    11
    Thanks Thanks Received 
    2
    Thanked in
    2 Posts
    Good morning @EPHRAIM,

    1) Which RSLogix do you have - it will show at the top of the program in the title bar, something like RSLogix 500, Micro, Micro Starter, Micro Starter Lite
    2) Try remote run mode
    3) Insure your PC is on the same subnet as your Ethernet PLC
    4)
    Try a different network cable

    Hope this helps,

    Shawn Tierney,
    Instructor at The Automation School

    Looking for affordable automation training? If you are, check out my courses at TheAutomationSchool.com!