Hi, uploading from AB 1400, notification pops, program in the process has changed
Hi please, am trying to upload a program from PLC AB 1400.after uploading, a message pops up asking me if I wish to go online,
when i accept another message pops up saying program in the processor has changed causing an offline state, do i want to upload ?
thank you for the reply sir,
If you select yes, does the same thing happen? once i press yes it goes gain asking me to create a new file, then save, after do you want to go online if yes the same information appears
If you say no, can you view the program offline? i cant without saving
Are you directly connected via Ethernet, or going through a switch which also connects to other devices? directly connected to Ethernet
What mode is the PLC in? RUN mode
What versions of Windows, RSLinx, RSLogix are you using? window 7 professional 32 bit, RSLinx 2.75, RSLogix 8.10.00 CPR 9
1) Which RSLogix do you have - it will show at the top of the program in the title bar, something like RSLogix 500, Micro, Micro Starter, Micro Starter Lite
2) Try remote run mode
3) Insure your PC is on the same subnet as your Ethernet PLC
4) Try a different network cable
Hope this helps,